Don said:----------------------------
----------------------------------------
Your point is true- the time interval is so small that for practical
purposes it can be ignored. I am not denying that. Obviously I gave that
impression- sorry for that.
I was simply pointing out that phil had it right in theory and Tony had it
wrong.
After this time for the wave to travel to the end and be reflected (and
other re-reflections die out) then conventional circuit theory is
applicable. The fact that the time is extremely small simply means that we
can pretend that it doesn't even exist.
While Matzloff is right in the time for a round trip is of the order of
200m, it is also dangerous to assume that one can ignore waves for shorter
distances. For example, a stroke to a tower of an EHV line (a lot less than
200m) will go down the tower, meet ground resistance and be reflected.
Such reflections have been found to be more likely to cause flashover than
direct strokes to the line (EPRI). Similarly, the practice in substations
is not "whole station" protection (where this is applicable, it must be done
considering a number of factors- quite interesting ) and putting specific
protection as near as possible to the protected apparatus-definitely within,
say, 10m. - It's not just the time to peak that is the critical factor. Do a
lattice diagram approach or use Bergeron's method (Hermann Dommel did a lot
of work with this at EPRI and has a lot of papers in IEEE- more dealing with
switching surges than lightning).
It's been a long time since I did any calculations in this area so I would
have to brush up.
I am real glad the probability of a direct house strike is low. I have
some appreciation for the earthing/bonding required in a substation
(also referred to by nobody).
Now - is this all germane to household protection? You say not and I agree
with you- because household equipment can ride through - at worst- doubling
of the clamped voltage for a very short time even though the clamped voltage
is relatively small compared to the peak of the incoming surge. --
The effect Martzloff was specifically looking for in experiments was
doubling of voltage.
As an aside, several of the experiments done by Martzloff were at EPRI.