Surge / Ground / Lightning

  • Thread starter Thread starter NB
  • Start date Start date
| (e-mail address removed) wrote:
|>
|> | Previously you said Martzloff "flubbed the experiment".
|>
|> I remember that. You were telling me about some information he had
|> obtained from some experiment.
|>
|> | Now you agree with Martzloff that branch circuit must be 200m for
|> | transmission line behavior with 1.2 microsecond rise time.
|>
|> That's not a result of an experiment.
|
| "*From this first test*, we can draw the conclusion (predictable, but
| too often not recognized in qualitative discussions of reflections in
| wiring systems) that it is not appropriate to apply classical
| transmission line concepts to wiring systems if ..."
|
| As usual, you don?t know what was written.

What what kind of surge did Martzloff use to carry out that test?


|> I'm not so sure the exact distance
|> is 200m for that exact rise time. But that is a subjective thing.
|
| Quit equivocating. Where is your cite. Like for nanosecond risetimes.

Observation.


|> | You say that doesn't apply because surges are faster. Martzloff uses 1.2
|> | us because that is a standard rise time for surges produced by lightning
|> | as defined in IEEE standards.
|>
|> Martzloff did not say that was a defined standard in the statement you
|> quoted. He just used it as an example to come up with the 200m figure.
|
| He used it because 1.2/50 (voltage) is an IEEE standard. The 8us from
| w_?s engineer is another standard (8/20 current).

The standard for what? The typical surge?


|> | w_' professional engineer source says 8 micoseconds with most of the
|> | spectrum under 100kHz.
|>
|> Even with 1 nanosecond rise time, most of the energy will be present in
|> the spectrum below 100 kHz. That means nothing when the surge is strong
|> enough to have energy above some frequency that is relevant to the whole
|> system involved that can do damage. That frequency might be 100 Mhz for
|> some thing, and 1 GHz for other things.
|
| Still missing ? your source. Nanosecond risetime. 100MHz spectrum.

Observation. Of course this is a concept you cannot understand.


|> | You still have *no sources that support your belief* that risetimes are
|> | far faster.
|>
|> I have experience and observation for that. I need no more.
|
| Lots of people have experience and observation with flying saucers.
|
| The rest of us want a source.

The only flying saucers I have seen are the ones I've tossed.
 
bud-- said:
Still missing - your source that indicates nanosecond rise times and
100MHz spectrum.



It is standard notation in the surge field. 1.2 us risetime and 50 us
duration
Sloppy notation.
 
but their
effectiveness when used on ungrounded outlets is reduced, since the path
to ground doesn't exist.

I was going to ask whether this would help protect delicate components
in any way, but of course, the neutral is earthed nearby anyways, and
the third earth wire is just a backstop?

jack
 
I was going to ask whether this would help protect delicate components
in any way,

Yes, as the surge protector is working to some extent, but it would work
far more effectively if it were plugged into a grounded outlet.

There's also the problem that using a surge protector in an ungrounded
outlet will cause the earth on the protector to rise in potential while
the protector is conducting a surge. Depending on the equipment plugged
into that strip, this has the potential to cause damage, as well as an
electrical shock to anyone touching a metal-cased appliance with a 3-pin
lead plugged into the strip.

Thus surge protectors should only be plugged into grounded outlets.
There will usually be a warning on the protector itself or in the user
instructions stating this.
but of course, the neutral is earthed nearby anyways, and
the third earth wire is just a backstop?

No. The earth pin, although bonded to neutral at the consumer unit
(=breaker box in US) should be regarded as a separate, third connection
from then on. The neutral is there to carry return current; the earth
is there for safety.
 
----------------------------
bud-- said:
The last standards for simulating typical surge waveforms I have seen
(IEEE) were
1.2 us rise time, 50 us duration
8 us rise time, 20 us duration
a ring wave with a frequency about 100kHz.

All are long relative to 0.2 microsecond, so wave propagation should not
be relevant for household circuits.
----------------------------------------
Your point is true- the time interval is so small that for practical
purposes it can be ignored. I am not denying that. Obviously I gave that
impression- sorry for that.

I was simply pointing out that phil had it right in theory and Tony had it
wrong.

After this time for the wave to travel to the end and be reflected (and
other re-reflections die out) then conventional circuit theory is
applicable. The fact that the time is extremely small simply means that we
can pretend that it doesn't even exist.

While Matzloff is right in the time for a round trip is of the order of
200m, it is also dangerous to assume that one can ignore waves for shorter
distances. For example, a stroke to a tower of an EHV line (a lot less than
200m) will go down the tower, meet ground resistance and be reflected.
Such reflections have been found to be more likely to cause flashover than
direct strokes to the line (EPRI). Similarly, the practice in substations
is not "whole station" protection (where this is applicable, it must be done
considering a number of factors- quite interesting ) and putting specific
protection as near as possible to the protected apparatus-definitely within,
say, 10m. - It's not just the time to peak that is the critical factor. Do a
lattice diagram approach or use Bergeron's method (Hermann Dommel did a lot
of work with this at EPRI and has a lot of papers in IEEE- more dealing with
switching surges than lightning).
It's been a long time since I did any calculations in this area so I would
have to brush up.

Now - is this all germane to household protection? You say not and I agree
with you- because household equipment can ride through - at worst- doubling
of the clamped voltage for a very short time even though the clamped voltage
is relatively small compared to the peak of the incoming surge. --

Don Kelly (e-mail address removed)
remove the X to answer
 
I'm curous to know how surge suppression can work without a ground
(earth) of any sort. Does the "black box" detect overvoltage and
disconnect the power like an earth leakage safety switch?

This might be fine for a TV, but surely not for a computer.

I don't recall any computer I've owned that did not have a three wire
connection to the mains. That and a MOV is OK for smallish surges, but
I believe that for a large surge, the sort that will blow a telephone
off the wall, one needs a large, short-path earth for the surge
detector to dump the extra power down.

I've got a few plug in protectors here and there to sop up a small
spike, but when a storm is within a few km, I pull the phone wire out
of the ADSL router, and the plug out of the mains. If I'm working at
the time, I might just keep a watch on the weather radar and count
lightning fashes to thunder times. It's rare that I get interrupted. I
have underground power and phone lines so that gives a little extra
protection, I believe.

This will address some of your questions only in summary. Details
are provided in other posts.

First, much of this stuff was learned by earliest 20th century
hams. They would disconnect their antenna, put the lead inside a
mason jar, and still suffer radio damage. Even mason jars could not
stop or block lightning. But then the antenna was earthed, then damage
stopped. It's just like Franklin's lightning rod (air terminal).
Protection has always been about diverting "it to ground, where it can
do no harm". Disconnecting did not provide sufficient protection.
That wire had to be earthed.

Protection for the TV, computer, and all other appliances is same.
Computers contain some of the most robust protection. Computer grade
UPSes can output electricity so dirty (when in battery backup mode) as
to even harm some small electric motors. But computers are so robust
as to make even that 'dirty' electricity irrelevant. Do not assume
computers have less internal protection. Intel ATX standards require
computers to be more robust than what is standard for other
appliances.

No protection exists by disconnecting - the black box. Air is a
best insulator. Lightning travels through 3 miles of air to contact
earth. What magic black box do you own that can stop what three miles
of sky could not? Protectors do not stop, block, or disconnect from
lightning. Furthermore, a lightning surge does damage too fast. A
fastest disconnect relay takes milliseconds. Lightning surges do
damage in microseconds. Two of so many reasons why protection is not
achieved by disconnecting.

Try damming a river to stop a flood. Dam gets swept away. Move
that dam off to the side; call it a dike. Open a large channel
downriver. Protecting by disconnecting, blocking, or absorbing surges
is akin to that dam - useless. Instead, install (and earth) a 'whole
house' protector - akin to a large channel downriver. And then
install dikes - internal protection inside appliances or other
supplementary protection.

Even dikes (supplementary protectors) are useless without that large
channel downriver - the properly earthed 'whole house' protector.

MOVs are routinely installed where direct lightning strikes are
earthed - without damage to MOVs. MOVs used in properly sized 'whole
house' protectors. But when a plug-in protector is sold to maximize
profits (not for protection), then grossly undersized protectors also
create another problem - scary pictures:
http://www.hanford.gov/rl/?page=556&parent=554
http://www.westwhitelandfire.com/Articles/Surge Protectors.pdf
http://www.ddxg.net/old/surge_protectors.htm
http://www.zerosurge.com/HTML/movs.html
http://tinyurl.com/3x73ol or
http://www3.cw56.com/news/articles/local/BO63312/

Routine is for direct lightning strikes to be earthed by a 'whole
house' protector. Routine is for a properly sized protector to earth
surges AND remain functional. A protector damaged by a direct
lightning strike - grossly undersized - is designed in direct
violation of MOV manufacturer's specs. MOV manufacturers are quite
clear about this. MOVs must only fail by degrading; not fail by
vaporizing. MOVs also do not work by sopping up surge energy. But
grossly undersizing a plug-in protector and a resulting explosive
damage gets the naive to recommend an obscenely overpriced protector.
Yes, grossly undersizing a protector can get the naive to recommend
more ineffective protectors.

An effective protector earths direct lightning strikes AND remains
functional. An effective protector means nobody knew the surge even
existed. But no explosive failure means some here would not recommend
that protector.

Above described secondary protection. Homeowners should also
inspect their primary inspection system:
http://www.tvtower.com/fpl.html

Buried wires do not provide effective protection. An industry
professional provides this application note. Notice even underground
wires must be earthed before entering the building. Even underground
wires can carry surges, destructively into the building. Any wire
that enters the building - overhead or underground - must connect to a
single point earth ground either directly (ie cable TV, satellite
dish) or via a protector (ie telephone, AC electric). The app note
shows two structures. Any wire into either structure first connects
to that structure's single point earth ground:
http://www.erico.com/public/library/fep/technotes/tncr002.pdf

And finally, it is posted multiple times including a reference to an
article for EE entitled "Protecting Electrical Devices from Lightning
Transients". That safety ground and neutral wire cannot provide
earthing for a long list of reasons.
 
Nobody described how much more earthing is installed in switching
centers (COs), electric substations, etc just to obtain a little
better earthing. A ten foot earth ground rod can be a massive
earthing improvement for surge protection. And then high reliability
facilities may spend $thousands more just to make that earthing but a
little better. Why so much extra conductors and labor for just a
little better ground? Because every little better earthing means that
much more surge protection. What makes a protector even more
effective? Better earthing.

So yes, where surge damage is not acceptable, then facilities will
do that much more work just to get a little better earthing. Earthing
is critical for direct lightning strikes without failure. Does that
mean a homeowner without a massive earthing mat should do nothing? Of
course not. Locating 3 meter ground rods (per post 1990 NEC
requirements) less than 10 feet from breaker box and telco provided
surge protector means significantly better protection. Anyone
building a new home should plan their surge protection where footings
are poured - see nobody's reference to cadwelding. Footings with
appropriately installed conductors (rebar) provide a home with
significant improvement (Ufer grounds). Protection should be planned
when the footings are poured. Better earthing (surge protection) for
so little money.

Nobody also discusses single point earth ground that is essential
for surge protection. Why? Again, a protector is only as effective
as its earth ground. Single point earth ground is essential to an
effective protector.

Some homeowners don't have that single point option due to failures
by the builder. One utility describes how to fix that defective
earthing:
http://www.cinergy.com/surge/ttip08.htm

Why do serious facilities do so much for their earthing system?
Earthing provides surge protection - where surge energy must be
harmlessly dissipated. And then, as Nobody notes, sometimes that
earthing system gets compromised by geology we did not know about.

What happens if damage occurs? We return to locate an earthing
defect. Even a nearby pipeline may adversely affect that earthing
system. If damage results, then discover a defect in the earthing
system. As Nobody demonstrates, so much labor to make earthing even
better because a surge protector is only as effective as that earth
ground.

BTW, battery racks do not absorb surge energy. Another concept even
taught in basic circuit theory - superposition. To surges, that
battery rack is equivalent to a short circuit. Batteries do not
absorb energy (if ignoring a battery's internal resistance). Those
batteries essentially connect surge currents to wires on both sides of
those batteries. To a surge, batteries are electrically equivalent to
a wire. Batteries are typically well earthed - meaning those
batteries will act just like a shunt mode surge protector - connecting
surge energy into earth. Batteries don't work as surge absorbers.
Batteries connect (shunt, divert, clamp) surge energy into earth.
 
The IEEE guide is aimed at "electricians, architects, technicians, and
electrical engineers who were not protection specialists."

IEEE and NIST state fundamental facts. Industry standard facts and
embarrassing questions.that Bud will ignore to lie and to promote plug-
in protector sales:

1) How does that plug-in protector provide protection without the
'always necessary' earth ground? What does a protector do? Bud
provides only two citations. Both disagree with his claims. The NIST
bluntly defines what a protector must do - Page 6:
You cannot really suppress a surge altogether, nor
"arrest" it. What these protective devices do is
neither suppress nor arrest a surge, but simply
divert it to ground, where it can do no harm.

Bud says his plug-in protectors somehow suppress or arrest surges.
Somehow, 'clamping to nothing' means that surge energy disappears?
Somehow protectors can work without earthing? NIST citation further
contradicts Bud on Page 17:
A very important point to keep in mind is that your
surge protector will work by diverting the surges to
ground. The best surge protection in the world can
be useless if grounding is not done properly.

2) Bud not only denies this also so important single point earth
ground. He also ignores what happens when a protector is too far from
earth and too close to appliances. Page 42 Figure 8: the surge
earthed 8000 volts destructively through appliances. This is the
second point from his citations that Bud must ignore.

3) So if a plug-in protector is effective protection, then
manufacturer specs will list each type of surge and protection from
that surge. Bud never provides that spec either. Why? Plug-in
protectors don't claim to protect from the type of surge that
typically causes damage. Not one plug-in protector manufacturer will
claim that protection - made obvious because Bud will not post those
specs and ignored over 400 requests for those specs.

4) No earth ground means no effective protection. A protector is
only as effective as its earth ground. Another reality that Bud must
ignore to post incessantly.

None of this is new. It is again posted because Bud continuously
ignores that even his own citations contradict him. Meanwhile w_tom
has provided many tens of professional citations that also contradict
Bud; that define how effective protection is routinely installed where
direct lightning strikes must not cause damage. We install effective
protection for lightning so that all other (and lesser) surges are
also made irrelevant. Surge protection is so routine for the past 100
years as to be traceable to human failure. Even the protector must
remain functional after a surge.
 
On properly grounded outlets, such a suppressor can deal with an
incoming surge on phase or neutral in an effective manner by conducting
and diverting current to the other leg AND to ground, but their
effectiveness when used on ungrounded outlets is reduced, since the path
to ground doesn't exist.

Include facts taught in first year electrical engineering OR
described in both 'top of the front page' articled in Electrical
Engineering Times on 1 Oct and 8 Oct 2007 entitled "Protecting
Electrical Devices from Lightning Transients" at:
http://www.planetanalog.com/showArticle.jhtml?articleID=201807127
http://www.planetanalog.com/showArticle.jhtml?articleID=201807830

That wire from wall receptacle is too long, has too many sharp
bends, has spliced, is bundled with other wires, etc. More reasons
why that safety ground wire is not earth ground wire. Protectors
without earth ground is not effective as Mike says. And AC wall
receptacle does not provide an earthing connection - wire too long -
too much impedance. Page 42 Figure 8 also demonstrates that problem
resulting in 8000 volts being earthing, instead, through the adjacent
TV.

Breaker box earthing wire goes over top of the foundation and drops
down to an earthing electrode. Compromised protection. Wire is too
long and has sharp bends. Better protection means wire goes through
foundation and down to that earthing electrode. Few meters less wire
and without those sharp bends means improved protection. Why? See
"Protecting Electrical Devices from Lightning Transients".

If earthng wire must be every meter shorter, then how does a
receptacle safety ground wire do earthing? Safety wire has maybe 30
or 50 sharp bends, numerous splices, and maybe 15 meters too long?
Low impedance connection to earth typically means 'less than 10
feet', or then even shorter for even better protection.

Obviously wall receptacle safety grounds do not provide earth
ground. But then Mike Tomlinson also did not understand the
engineering numbers in that EE Times article entitled "Protecting
Electrical Devices from Lightning Transients". Note the numbers.
Wall receptacle safety grounds cannot provide a low impedance
connection to earth ground. Engineers would know this. Mike
Tomlinson obviously does not.

Literally every incoming wire must make that short (low impedance)
connection to earth ground. If that earthing wire is not separated
from other wires (if that earthing wire is inside a bundle of romex
cables), then that earthing wire induces surges on those other wires.
Just another reason why safety ground is not earth ground. Just
another engineering fact that Mike Tomlinson read and did not
understand.

AC wall receptable is not an effective earth ground. Protectors
best make a less than 3 meter (low impedance) connection to earth
which wall receptacles just cannot provide.
 
It is those nuances that w_twat fails to explain when he spouts his one-
cure-for-all-ills religious mantra about every dwelling absolutely
requiring whole-house surge protection.

Mike Tomlinson has just posted in agreement. UK homes typically do
not need what is necessary in FL homes. UK homes need not be earthed
as central FL homes may be earthed:
http://members.aol.com/gfretwell/ufer.jpg

Many homes have more than enough protection with only one earthed
'whole house' protector - and nothing else. Especially in the UK.
That means spending tens (or maybe one hundred) times less money for
protection of everything.

UK homes may be more than sufficiently earthed with one 3 meter
ground rod. Then one surge protector can provide more than sufficient
protection for everything - eliminating maybe £500 or £2000 for plug-
in protectors.
 
The same thing we did in the studios and transmitter sites. Use a
combination of protection at the building's main disconnect, and
individual protection at each critical device. The only thing that I've
lost in the last ten years was when lightning hit a huge pine tree, and
cut the top half of it off. It landed on the ground right over the
buried telephone line, and a second strike blew out the modem and MOV
protection on the phone line.

You suffered damage from a lightning strike and call that effective
protection? Modems are most typically damaged by surges entering an
AC mains. Outgoing surge path would be the phone line to earth via a
telco installed 'whole house' protector. Damage from lightning is
effective protection? After spending how much for all those
protectors, you call that protection?

Phone lines do not use MOV protectors. Basic information that you
would have learned if not wasting time insulting people. MOVs have
too much capacitance. Phone line 'whole house' protectors use other
technologies with lower capacitance.
 
| Now - is this all germane to household protection? You say not and I agree
| with you- because household equipment can ride through - at worst- doubling
| of the clamped voltage for a very short time even though the clamped voltage
| is relatively small compared to the peak of the incoming surge. --

What if the surge is an extreme case (e.g. direct strike very near) and it is
arriving at protection devices in common mode (same polarity on all three
wires). Bud's assertion _seems_ to be that no surge could ever be of the
type with substantial energy at high frequencies. My belief is that they
can, and will at times. Lightning strokes have that energy, or else you
would not receive them on UHF. If the stroke is strong _and_ close (e.g.
less line inductance between the point of strike and where it is being
considered), then more of that UHF energy will arrive.

I have seen damage patterns in electronics that strongly suggests that there
were specific paths involved based on minor levels of reactance in the circuit.
A resistor would be melted along one path, but not so along another which had
a small inductor (3 turns in air) in the way. And this device (a VCR) was on
a surge protector along with a TV that was unharmed.

If Bud is just arguing about the _typical_ (median?) surge level, then maybe
we are arguing apples and oranges. I certainly don't intent to protect against
50% of surges. My target is better than 99%. I want to feel comfortable
sleeping through a severe thunderstorm while my computers and media center
remain plugged in.

I do agree that things can survive at the clamping voltage. But there has to
be a clamping situation. It's too easy for a surge to come in as a common
mode surge where the voltage difference across the MOVs would be (nearly) zero.
Then all we have is a propogating wavefront. And if it is strong and/or close
then we have very fast rise times. And it passes by the MOVs "laterally".

There's probably a big difference of opinion about just how much protection is
worth it. But one thing I do see in at least part of this thread is that Bud
focuses on quoting things other people say, and does very little to express
things in his own words. That suggests he reads but does not fully understand.
And that means I can't ask questions of what is said in the thread. Since Bud
can't (or won't) defend what he's saying in his own words based on his own
knowledge, it's not really a two way street. His "experts" are not involved
in the debate; they can neither defend their position nor be questioned about
it to get more details.

It also has brought some other comments from people who are either anti-social
insulting types, or those that just don't understand what is said (apparently
having never dealt with transmission line propogation), or both. But at least
I know who not to trust any technical opinions from when I have question to
ask about things I want to learn more about.
 
..com> said:
Mike Tomlinson has just posted in agreement.

As usual, you're twisting things again. I'm certainly not agreeing with
_you_.
UK homes typically do
not need what is necessary in FL homes.

instead, YOU are agreeing with what I said...
UK homes need not be earthed
as central FL homes may be earthed:
http://members.aol.com/gfretwell/ufer.jpg

Those pictures do absolutely nothing to bolster your argument,
especially appearing as they do without any explanatory text.
Many homes have more than enough protection with only one earthed
'whole house' protector - and nothing else. Especially in the UK.

Nonsense. You live in Pennsylvania (thankfully, though I do feel sorry
for your neighbours and anyone else with whom you come into contact.)
It is not common practice to install whole-house protectors in the UK.
UK homes may be more than sufficiently earthed with one 3 meter
ground rod.

You have no idea. TT earthing (ground rod earthing) is relatively
unusual in the UK. The majority of buildings have a T-N-C-S supply from
the utility provider, who provide an earth point alongside the supply
cable where it rises out of the ground.
Then one surge protector can provide more than sufficient
protection for everything - eliminating maybe £500 or £2000 for plug-
in protectors.

Absolute crap. You have no idea how much surge protectors in the UK
cost.

w_ once again lies, distorts, and twists what others say to suit his own
bizarre beliefs and ideologies.

w_ continues to lead his one-man crusade and is unable to understand why
his dogmatic posts attract contempt and derision from many different
people with a wide spectrum of experience and knowledge of electrical
and electronic theory and practice.

w_ continues to believe that he alone is Right and everyone else is
Wrong, a classic sign of a sociopathic personality. w_twat needs to
consult a mental health professional.
 
I wonder why, since electrical codes in North America
and Britain require a ground connection at each outlet;
computer power cords are 3 wire?


(snip)

hot neutral ground
I suppose I phrased the question badly. I wonder why a surge
would wander around looking for ground, when its available
in the box!
 
? said:
I'm on 2000' of sand, and at the moment, my house earth is the copper
2000'? I am only 5'10":-)
water pipes, but the water corp keep adding plastic bits here and
there, so I don't really trust it. I was going to hammer in a 20'
length of 3/4" copper pipe under a large tree which gets the drain
from my grey water. Probably the best I can do.
Perhaps you should get a proper earthing electrode, with a spiked end and a
stell core? It would be really difficult to hammer 20' of 3/4" copper pipe.
They are not that expensive.
I'm not a full bottle on earth loops yet so i don't know about leaving
the water mains connection still connected.
The earth loops matter only in electronic circuits, like amplifiers and the
like. In electricity, the play no role, in fact they reduce even further the
earth resintance.
What's the best way to test an earth?
I heard once that a large electric radiator (fire) connected between
active (hot) and the earth will glow as per normal if the earth has
good capacity. Perhaps a current comparison between the earth return
and neutral return would be more informative?
Although the neutral is at zero potential, still carries a large current.
The earth not. Since the neutral point of the LV side of the local
substation is earthed, for the electricity "is all the same" between neutral
and earth, depending on the neutral earthing system.
 
| (e-mail address removed) wrote:

|> | w_' professional engineer source says 8 micoseconds with most of the
|> | spectrum under 100kHz.
|>
|> Even with 1 nanosecond rise time, most of the energy will be present in
|> the spectrum below 100 kHz. That means nothing when the surge is strong
|> enough to have energy above some frequency that is relevant to the whole
|> system involved that can do damage. That frequency might be 100 Mhz for
|> some thing, and 1 GHz for other things.
|
| Still missing - your source. Nanosecond risetime. 100MHz spectrum.

Observation. Of course this is a concept you cannot understand.

Observation proves flying saucers and magic.

Without supporting sources it is Phil's Phantasy Physics.
Where is a source that supports your belief in nanosecond risetimes and
100MHz spectrum?
 
| Now - is this all germane to household protection? You say not and I agree
| with you- because household equipment can ride through - at worst- doubling
| of the clamped voltage for a very short time even though the clamped voltage
| is relatively small compared to the peak of the incoming surge. --

My belief is that they
can, and will at times.

People believe in flying saucers.
Where is a source that supports your belief?
I do agree that things can survive at the clamping voltage. But there has to
be a clamping situation. It's too easy for a surge to come in as a common
mode surge where the voltage difference across the MOVs would be (nearly) zero.
Then all we have is a propogating wavefront. And if it is strong and/or close
then we have very fast rise times. And it passes by the MOVs "laterally".

Where is a source that supports your belief in nanosecond risetimes and
100MHz spectrum?
But one thing I do see in at least part of this thread is that Bud
focuses on quoting things other people say, and does very little to express
things in his own words.

I focus on the real world. You focus on your beliefs.

Where is a source that supports your belief in nanosecond risetimes and
100MHz spectrum?
 
w_tom said:
Industry standard facts and
embarrassing questions.that Bud will ignore to lie and to promote plug-
in protector sales

Lacking any valid technical arguments poor w_ has to try to discredit
opponents. My only association with surge protectors is I have some.
1) How does that plug-in protector provide protection without the
'always necessary' earth ground? What does a protector do? Bud
provides only two citations. Both disagree with his claims. The NIST
bluntly defines what a protector must do - Page 6:

What does the NIST guide really say about plug-in suppressors?
They are "the easiest solution".
2) Bud not only denies this also so important single point earth
ground.

If w_ could only read he would have seen my emphasis on a *short*
'ground' wire from phone/cable entry protectors to the 'ground' at the
power service. w_ appears to want all wires run to the grounding
electrode. That does not provide the minimum voltage between power and
signal wires. Martzloff has written "the impedance of the grounding
system to 'true earth' is far less important than the integrity of the
bonding of the various parts of the grounding system."

And the case where phone/cable entry points are too far distant from
power service, IEEE guide says "the only effective way of protecting
the equipment is to use a multiport [plug-in] protector."
He also ignores what happens when a protector is too far from
earth and too close to appliances. Page 42 Figure 8: the surge
earthed 8000 volts destructively through appliances. This is the
second point from his citations that Bud must ignore.

The illustration has 2 TVs. The IEEE says the point of the illustration
is "to protect TV2, a second multiport protector located at TV2 is
required." Way to complicated for w_.
3) So if a plug-in protector is effective protection, then
manufacturer specs will list each type of surge and protection from
that surge. Bud never provides that spec either.

"Each type of surge" is nonsense. w_'s favored SquareD service panel
suppressors do not have specs for "each type of surge". Lacking valid
technical arguments has to invent problems.
Plug-in
protectors don't claim to protect from the type of surge that
typically causes damage.

Complete nonsense.
Not one plug-in protector manufacturer will
claim that protection - made obvious because Bud will not post those
specs and ignored over 400 requests for those specs.

Over 400 requests - another hallucination.
Specs posted often and ignored.
4) No earth ground means no effective protection. A protector is
only as effective as its earth ground.

w_'s religious belief (immune from challenge) in earthing has been the
elephant in the closet. w_ believes a surge protector must directly
earth a surge. Thus in his view plug-in suppressors (which are not well
earthed) can not possibly work.

The IEEE guide explains plug-in suppressors work by CLAMPING the voltage
on all wires (signal and power) to the common ground at the suppressor.
The voltage between the wires going to the protected equipment is safe
for the protected equipment. Plug-in suppressors do not work primarily
by earthing (or stopping or absorbing). The guide also explains earthing
does occur, just not primarily through the plug-in suppressor. (Read the
guide starting pdf page 40).

For accurate information on surges read the IEEE and NIST guides. Both
say plug-in suppressors are effective.

There are 98,615,938 other web sites, including 13,843,032 by lunatics,
and w_ can't find another lunatic that says plug-in suppressors are NOT
effective. All you have is w_'s opinions based on his religious belief
in earthing.

Embarrassing questions that w_ will ignore:
- Why do the only 2 examples of surge suppression in the IEEE guide use
plug-in suppressors?
- Why does the NIST guide says plug-in suppressors are "the easiest
solution"?
- Why do all but one of w's "responsible manufacturers" make plug-in
suppressors?
- Why does SquareD say in addition to their "whole house" suppressors
"electronic equipment may need additional protection" from plug-in
suppressors.
- Why aren't airplanes crashing daily when they get hit by lightning (or
do they drag an earthing chain)?
 
w_tom said:
Mike Tomlinson has just posted in agreement. UK homes typically do
not need what is necessary in FL homes. UK homes need not be earthed
as central FL homes may be earthed:
http://members.aol.com/gfretwell/ufer.jpg

Many homes have more than enough protection with only one earthed
'whole house' protector - and nothing else. Especially in the UK.
That means spending tens (or maybe one hundred) times less money for
protection of everything.

UK homes may be more than sufficiently earthed with one 3 meter
ground rod. Then one surge protector can provide more than sufficient
protection for everything - eliminating maybe £500 or £2000 for plug-
in protectors.

Last I heard UK phone entry protectors did not clamp the voltage to
earth. That allows high voltage between power and phone wires. w_’s
favored service panel suppressor provides no protection from this hazard.
 