A PC power supply is nothing like a voltage regulator. It will not
stop your computer from rebooting when your lights blink and your
speakers pop.

But you remain blissfully ignorant...
 
John said:
A PC power supply is nothing like a voltage regulator. It will not
stop your computer from rebooting when your lights blink and your
speakers pop.

But you remain blissfully ignorant...

The ATX supply *is* a regulating device. The duty cycle
of the switching stage, varies according to load. Notice the
word "feedback" in the schematic here - that is how the
supply checks the output voltage, and adjusts the output
voltage to maintain the correct value. The adjustment is
made by varying the duty cycle of the switching stage.

http://www.pavouk.org/hw/en_atxps.html

The ATX supply, can maintain correct output voltages, while
the input is 90-120VAC. That means, even under input brownout, the
supply continues to function. It could operate over a wider range
than that, but for the need to have an undervoltage lockout
to protect the switching transistors.

Say the DC output of the supply, is currently drawing 120 watts.
On the AC input, we'd guess the supply was using 120V @ 1 amp.
If the AC voltage suddenly dropped to 60V and there was no UVLO,
the supply would draw 2 amps (60V * 2A primary side, to make 120W
for the secondary side). The equivalent of those two amps (a
doubling of current), would be needed in the primary switching
transistors. And if continued unchecked, the switcher would
be handling too large currents for comfort. So at some point,
switching converters should switch themselves off, and limit
operation to an acceptable range.

*******

In terms of holdup time (the time the supply can provide DC
output), that is a function of output loading.

The spec sheet for the supply, will say it can provide full
load current, for 16 milliseconds or more. The primary side
capacitor, is made big enough, to protect it against line
transients (transients where the voltage goes to zero for
periods of milliseconds). The holdup time is generally
enough, to make it compatible with the cheapest UPS types
(standby UPS). A standby UPS needs some time to switch
to battery, during which the AC output will be zero.

Utility power Running on battery
Standby UPS ----------------+ +-----------
| |
+-----------+
notices power
is out

ATX primary cap ---------------___ +---------
\___ |
\___ |
\_|


No glitch or variation
ATX DC outputs --------------------------------------
Why? Because it's regulated

At the other extreme, if your PC is sleeping, and the
motherboard is only using +5VSB rail, the power supply
can maintain a correct 5V level on +5VSB, for 30 seconds
or longer. So if the AC power goes off for a few seconds
while the computer is sleeping, you won't lose your session
stored in RAM. It's good for times in the vicinity of
thirty seconds or so. That's how long mine can go, before
the +5VSB LED goes off on the motherboard.

Paul
 
Paul said:
John Doe wrote:

The ATX supply *is* a regulating device.

Of course it is, but IT IS NOTHING LIKE A LINE VOLTAGE REGULATOR
that includes a big heavy transformer.

You should know better.

--










The duty cycle
of the switching stage, varies according to load. Notice the
word "feedback" in the schematic here - that is how the
supply checks the output voltage, and adjusts the output
voltage to maintain the correct value. The adjustment is
made by varying the duty cycle of the switching stage.

http://www.pavouk.org/hw/en_atxps.html

The ATX supply, can maintain correct output voltages, while
the input is 90-120VAC. That means, even under input brownout, the
supply continues to function. It could operate over a wider range
than that, but for the need to have an undervoltage lockout
to protect the switching transistors.

Say the DC output of the supply, is currently drawing 120 watts.
On the AC input, we'd guess the supply was using 120V 1 amp.
If the AC voltage suddenly dropped to 60V and there was no UVLO,
the supply would draw 2 amps (60V * 2A primary side, to make 120W
for the secondary side). The equivalent of those two amps (a
doubling of current), would be needed in the primary switching
transistors. And if continued unchecked, the switcher would
be handling too large currents for comfort. So at some point,
switching converters should switch themselves off, and limit
operation to an acceptable range.

*******

In terms of holdup time (the time the supply can provide DC
output), that is a function of output loading.

The spec sheet for the supply, will say it can provide full
load current, for 16 milliseconds or more. The primary side
capacitor, is made big enough, to protect it against line
transients (transients where the voltage goes to zero for
periods of milliseconds). The holdup time is generally
enough, to make it compatible with the cheapest UPS types
(standby UPS). A standby UPS needs some time to switch
to battery, during which the AC output will be zero.

Utility power Running on battery
Standby UPS ----------------+ +-----------
| |
+-----------+
notices power
is out

ATX primary cap ---------------___ +---------
\___ |
\___ |
\_|


No glitch or variation
ATX DC outputs --------------------------------------
Why? Because it's regulated

At the other extreme, if your PC is sleeping, and the
motherboard is only using +5VSB rail, the power supply
can maintain a correct 5V level on +5VSB, for 30 seconds
or longer. So if the AC power goes off for a few seconds
while the computer is sleeping, you won't lose your session
stored in RAM. It's good for times in the vicinity of
thirty seconds or so. That's how long mine can go, before
the +5VSB LED goes off on the motherboard.

Paul
Path: news.astraweb.com!border6.newsrouter.astraweb.com! news.astraweb.com!border5.newsrouter.astraweb.com!news.glorb.com!
eternal-september.org!feeder.eternal-september.org!mx04.eternal-
september.org!.POSTED!not-for-mail
From: Paul <nospam needed.com>
Newsgroups: alt.comp.hardware.pc-homebuilt
Subject: Re: Users that have a UPS but no data backup
Date: Sun, 18 Dec 2011 01:07:11 -0500
Organization: A noiseless patient Spider
Lines: 75
Message-ID: <jcjvue$j6u$1 dont-email.me>
References: <4ec33072$0$20154$c3e8da3$88b277c5 news.astraweb.com>
<ghi6c7hqt45648cavjooqplh0c8r88hjfp 4ax.com>
<9l8oe79rk3oaa9dcu2k6j6h0c67cruesig 4ax.com> <4eecd0a8$0$32067
$c3e8da3$40d4fd75 news.astraweb.com>
<ujppe7tt6hgolq7isr65lspgecosua6anm 4ax.com> <4eecf7e5$0$2213$c3e8da3
$a9097924 news.astraweb.com> <qjaqe7tfna6spes8m9dn21eohhur9bpquk
4ax.com> said:
Mime-Version: 1.0
Content-Type: text/plain; charset=ISO-8859-1; format=flowed
Content-Transfer-Encoding: 7bit
Injection-Date: Sun, 18 Dec 2011 06:07:10 +0000 (UTC)
Injection-Info: mx04.eternal-september.org; posting-
host="fOuyM3XaxtxsDZx5t76fEg"; logging-data="19678"; mail-complaints-
to="abuse eternal-september.org"; posting-account="U2FsdGVkX1
+HRXtQD9maz9Pj8ITiZPuSx4elflMb22k="
 
Back
Top