I can believe the voltage. See my reply to w_tom. A surge protector isMrB said:Mr w-tom,
You were not there. 220 volts was measured on the line with a digital
voltmeter. Believe what you want, it happened. My main point was that most
of the computers survived with minor or no damage, even though the surge
protectors blew out. It was good protection for the price.
MrB
designed to protect from very short spikes, not sustained high voltage.
They usually "blow" after carrying enough current to cause them to destruct,
allowing them to become an open circuit. Since they are placed across the
incoming line, the line voltage will remain the same after their destruction.
Many surge protectors contain their own over current protection. The MOVs
could well draw enough current to trip this device before they themselves
were destroyed. This would protect the attached loads, and could well leave
the line circuit breaker untripped. In this case, with the load being removed,
the line voltage would be close to 220 V, even with a small load on the other
side of the circuit, since the voltmeter draws very little current.
The ground wire has nothing to do with what happens with an open neutral.
It's only purpose is for safety. It is connected to the neutral(s) only
at the service entry point. If the neutral becomes open, the return path
for the circuit is through the load on the other side of the 120/240 V
circuit to the other "hot" wire, with 240 V between the two "hot" wires.
Virg Wall
--