| Believe whatever you like, but typically it's just a bridge
| rectifier, then a voltage doubler in 110VAC locations, so
| it's 2 x diode drop of about 0.7V. You still have to have a
| capacitor, though perhaps a smaller capacity would suffice
| if the power were already DC. That combined with removal of
| the bridge rectifier isn't much cost or space savings. Some
| AC filtration circuitry could also be reduced or removed but
| not all of it. These parts are only a small % occupancy of
| the real-estate in a PSU.
Sure, it's not a great deal of advantage to remove them. But
it's definitely more than 1% of the wasted power.
|>Where there's dissipation, there is efficiency gained if that part can be
|>eliminated without incurring that cost elsewhere (but that may be an issue
|>in the data center to convert its incoming 3 phase 480VAC to 400VDC and
|>managing the paralleling with the battery banks).
|
| yes but only a minimal amount of efficiency gained. There
| are lots of other ways to reduce power consumption so it is
| stretching a point too far.
There are lots of things that can be done with minimal efficiency
improvements. Do them all and you get a lot.
|>| Further, commodity grade electrical supply line wire is not
|>| very expensive relative to most other components, the loss
|>| on the (existing AC, or per your idea going to DC) supply
|>| wiring is also negligible.
|>
|>It's not too bad at 120VAC, though a it better at 240VAC (which I would
|>prefer to use). But a design around 12VDC would be some very big wires.
|
| ??? Who suggested using a 12VDC whole-site supply? It's
| non-applicable.
It has been suggested as a means to make use of car or golf cart
batteries. At least 12VDC is interruptible by circuit breaker
reasonably easy.
| The topic was using existing mains supply infrastructure or
| moving to something proprietary for a supposed gain. Also,
| you are ignoring that converting from the mains AC to this
| HV, ~ 400VDC is not without losses. It still has to be
| rectified, did you propose using synchronous rectification
| (which has more benefit vs cost in lower voltage
| applications) or continuing to use a bridge rectifier? If a
| bridge, you have lower power loss with individual bridge
| rectifiers in each system PSU than only one for the entire
| site HD DC, since voltage drop rises with a current
| increase.
I'm not suggesting any of these things specifically. I'm just
pointing out the various aspects people who want to look into
the things they can do should take a look at (or not).
My own plans for a better electrical system for my computers is
to use a 240VAC system.
|>|>But such a setup would be far too hazardous for typical home use
|>|>(that is, not something sold commercially for a consumer market, even
|>|>though an engineer hobbyist might have no problem with it).
|>|
|>|
|>| It would be impractical and expensive, but the hazard not
|>| significantly different than present 110/220V AC delivery
|>| systems. All that to save a trivial amount of power.
|>
|>Such a system can be made safe by competent electricians. But for homes,
|>the standards have to consider do-it-yourself-ers doing the wiring.
|
| It would not be more hazardous to any significant extent,
| it's not as though a DIYer doesn't have to use same methods
| for 110/220V.
If things are kept entirely in a metal box and properly constructed,
the hazard is under control. But running high voltage DC through the
building poses serious hazard issues that need to be designed very
carefully (especially with respect to electrical code compliance).
|>DC is not as easy to interrupt as AC. And your fault current from a central
|>PSU might not have enough to work the breakers properly.
|
| The current isn't THAT much lower, if all these proprietary
| supply parts were being installed it would simply be a
| matter of also sourcing suitable breakers.
The types of breakers needed for equipment supplementary protection are
quite different than those needed for structural wiring. If you keep
all the DC wiring out of the structure, then you can use cheaper circuit
breakers.
Try checking the UL listed voltage ratings of breakers for AC vs. DC.
|>Even common DC to 120VAC inverters are dangerous for homes because such
|>inverters can't properly trip circuit breakers when there is a short on
|>the AC side.
|
| There's no need for them to trip a home circuit breaker
| until the current exceeds a safe level to that inverter.
| Instead they have internal fuses, it is shutting off the
| device with a problem instead of the entire AC circuit,
| exactly the solution you'd want.
|
| Not dangerous, optimal.
I'm referring to inverters that produce AC output feeding the structural
wiring of a building like a home. A short circuit in the wiring will not
produce anywhere near the current flow that would happen if you shorted
the same wiring when fed by utility power. In the case of utility power,
when you cross the wires together, you get a nice blue flash that quits
instantly as the breaker's magnetic trip kicks it off within a half cycle
(and the arc breaks at the zero crossing, if not before). The current
would be a low hundreds to low thousands of amps, depending of many factors
like transformer capacity, wire length, etc. Magnetric trips in circuit
breakers are set to at high levels like 80 amps and up. If they were set
lower, then starting motors would be tripping breakers all the time. In
industrial settings, breakers are even adjustable. Cheap home breakers
have fixed settings for the magnetic trip (the one that works fast). If
there is a low level of overload, the thermal trip will eventually get it,
but it takes time to warm up and bend metal enough to release teh spring
energy to open the circuit. Inverters cannot deliver the high current
levels to start bit motors or trip magnetic elements of circuit breakers.
So if you cross the wires when an inverter is in use, instead of that
bright blue flash, your get a small sizzling arc that keeps on going for
a minute or two. Shorts caused by wiring damage would end up starting a
fire given the time involved. Arc-fault breakers might be usable to solve
this issue (and they are being more widely required in the 2008 electrical
code).
| rectifier, then a voltage doubler in 110VAC locations, so
| it's 2 x diode drop of about 0.7V. You still have to have a
| capacitor, though perhaps a smaller capacity would suffice
| if the power were already DC. That combined with removal of
| the bridge rectifier isn't much cost or space savings. Some
| AC filtration circuitry could also be reduced or removed but
| not all of it. These parts are only a small % occupancy of
| the real-estate in a PSU.
Sure, it's not a great deal of advantage to remove them. But
it's definitely more than 1% of the wasted power.
|>Where there's dissipation, there is efficiency gained if that part can be
|>eliminated without incurring that cost elsewhere (but that may be an issue
|>in the data center to convert its incoming 3 phase 480VAC to 400VDC and
|>managing the paralleling with the battery banks).
|
| yes but only a minimal amount of efficiency gained. There
| are lots of other ways to reduce power consumption so it is
| stretching a point too far.
There are lots of things that can be done with minimal efficiency
improvements. Do them all and you get a lot.
|>| Further, commodity grade electrical supply line wire is not
|>| very expensive relative to most other components, the loss
|>| on the (existing AC, or per your idea going to DC) supply
|>| wiring is also negligible.
|>
|>It's not too bad at 120VAC, though a it better at 240VAC (which I would
|>prefer to use). But a design around 12VDC would be some very big wires.
|
| ??? Who suggested using a 12VDC whole-site supply? It's
| non-applicable.
It has been suggested as a means to make use of car or golf cart
batteries. At least 12VDC is interruptible by circuit breaker
reasonably easy.
| The topic was using existing mains supply infrastructure or
| moving to something proprietary for a supposed gain. Also,
| you are ignoring that converting from the mains AC to this
| HV, ~ 400VDC is not without losses. It still has to be
| rectified, did you propose using synchronous rectification
| (which has more benefit vs cost in lower voltage
| applications) or continuing to use a bridge rectifier? If a
| bridge, you have lower power loss with individual bridge
| rectifiers in each system PSU than only one for the entire
| site HD DC, since voltage drop rises with a current
| increase.
I'm not suggesting any of these things specifically. I'm just
pointing out the various aspects people who want to look into
the things they can do should take a look at (or not).
My own plans for a better electrical system for my computers is
to use a 240VAC system.
|>|>But such a setup would be far too hazardous for typical home use
|>|>(that is, not something sold commercially for a consumer market, even
|>|>though an engineer hobbyist might have no problem with it).
|>|
|>|
|>| It would be impractical and expensive, but the hazard not
|>| significantly different than present 110/220V AC delivery
|>| systems. All that to save a trivial amount of power.
|>
|>Such a system can be made safe by competent electricians. But for homes,
|>the standards have to consider do-it-yourself-ers doing the wiring.
|
| It would not be more hazardous to any significant extent,
| it's not as though a DIYer doesn't have to use same methods
| for 110/220V.
If things are kept entirely in a metal box and properly constructed,
the hazard is under control. But running high voltage DC through the
building poses serious hazard issues that need to be designed very
carefully (especially with respect to electrical code compliance).
|>DC is not as easy to interrupt as AC. And your fault current from a central
|>PSU might not have enough to work the breakers properly.
|
| The current isn't THAT much lower, if all these proprietary
| supply parts were being installed it would simply be a
| matter of also sourcing suitable breakers.
The types of breakers needed for equipment supplementary protection are
quite different than those needed for structural wiring. If you keep
all the DC wiring out of the structure, then you can use cheaper circuit
breakers.
Try checking the UL listed voltage ratings of breakers for AC vs. DC.
|>Even common DC to 120VAC inverters are dangerous for homes because such
|>inverters can't properly trip circuit breakers when there is a short on
|>the AC side.
|
| There's no need for them to trip a home circuit breaker
| until the current exceeds a safe level to that inverter.
| Instead they have internal fuses, it is shutting off the
| device with a problem instead of the entire AC circuit,
| exactly the solution you'd want.
|
| Not dangerous, optimal.
I'm referring to inverters that produce AC output feeding the structural
wiring of a building like a home. A short circuit in the wiring will not
produce anywhere near the current flow that would happen if you shorted
the same wiring when fed by utility power. In the case of utility power,
when you cross the wires together, you get a nice blue flash that quits
instantly as the breaker's magnetic trip kicks it off within a half cycle
(and the arc breaks at the zero crossing, if not before). The current
would be a low hundreds to low thousands of amps, depending of many factors
like transformer capacity, wire length, etc. Magnetric trips in circuit
breakers are set to at high levels like 80 amps and up. If they were set
lower, then starting motors would be tripping breakers all the time. In
industrial settings, breakers are even adjustable. Cheap home breakers
have fixed settings for the magnetic trip (the one that works fast). If
there is a low level of overload, the thermal trip will eventually get it,
but it takes time to warm up and bend metal enough to release teh spring
energy to open the circuit. Inverters cannot deliver the high current
levels to start bit motors or trip magnetic elements of circuit breakers.
So if you cross the wires when an inverter is in use, instead of that
bright blue flash, your get a small sizzling arc that keeps on going for
a minute or two. Shorts caused by wiring damage would end up starting a
fire given the time involved. Arc-fault breakers might be usable to solve
this issue (and they are being more widely required in the 2008 electrical
code).