VanguardLH said:
Paul wrote on 2014/05/31:
Wordpad also shows .rtf file (that's typically the app used in Windows
to create .rtf files since MS Word will normally create .doc files).
Without the cable running from the computer to the UPS, the UPS will
never know the computer wants to shutdown when the power level reaches a
minimum threshold. The UPS won't know anything about how power options
for a UPS are configured in the OS without a signal coming back to the
UPS. So the UPS just stays up until it drains (some have their own
config panels in the UPS to regulate thresholds but I doubt this one has
those features or, if it does, the OP never set the config inside the
UPS).
No matter what, that UPS will switch off at 10.5V. It's independent
of anything else. It doesn't matter what protocol is running on that
cable, basic unidirectional warning status indicators, or full protocol,
the inverter will not go below 10.5V.
There are two reasons to stop an inverter running off a 12V battery.
1) Discharging battery below the knee of each cell. The knee is defined
as a point, where most of the available energy has been extracted
from the battery. So little capacity (watt-hours) are left in the battery
below 10.5V, it is pointless to attempt to "milk" them. The inverter
shuts off, to protect the battery. At least some lead acid batteries,
do not tolerate deep discharge well.
2) The inverter shuts off, to protect itself. The inverter effectively
runs at constant power on the output. It is supplying, say, 120V @ 1A
or 120W. On the input, it takes 12V @ 10A to supply the energy (numbers
adjusted for easy math). Now, imagine you let the inverter discharge
the battery source to 6V. The primary current grows to 20A. This is
hard on the primary side components. And if the output of the UPS
was "running at max", now the primary side is running at "double max".
The input switching transistors now have to be made bigger, for this
ridiculous situation. Consequently, to protect the inverter from runaway
input current (caused by the feedback attempting to maintain the output
level), the inverter shuts off to protect itself. On the telecom equipment
we made at work, which connects to a -48V battery room, this is UVLO or
undervoltage lockout. When shopping for converters, we would be looking
for UVLO as a mandatory feature. (Converter type known as point of use
power supplies.)
http://en.wikipedia.org/wiki/Undervoltage-lockout
If a UPS runs a battery flat, in some cases it was because the
battery was actually worn out, and even with no load, just winks out
on its own. But just as likely, something is wrong with the hardware.
In the case of the hundred or so UPS we bought for individual designer
workspaces at work, about ten of those were defective out of the box. And
the defect on each unit was not the same. Each had its own symptoms. For example,
one of the defective ones would stay on battery, even when the AC came back.
A hardware defect in the unit, an inability to trigger on low battery,
is a reason for the thing to trash the battery.
HTH,
Paul