coolsti said:
Can anyone with knowledge/experience give some advice regarding the
purchase of an UPS for our home computers?
Our main concern is to set up an UPS as protection against surges caused
by lightning. We don't really care how long the UPS can maintain the
computers running in the event of a power outage.
The main question is what size UPS do we require? We have two Pentium 4
PC's (2.4GHz + 3GHz) loaded with the usual peripherals (DVD/CD drives, 2
hardisks each) and two CRT monitors (19" and 17"). We also have a laser
printer and small hardware firewall.
We would like to keep the cost of a UPS down as much as possible. Can
anyone help with an idea as to the rating that we could get by with for
lightning surge protection? And a good tip on UPS model?
If the expense is too high to cover all equipment, we could also consider
protecting just the PC's and leaving the monitors and printer off the UPS.
Thanks for any help!
Steve, Denmark
There is a selection tool here. The laser printer would generally
not be connected, as it would likely double the size of UPS you
would need to buy.
http://www.apc.com/tools/ups_selector/index.cfm
UPS are rated in watts and volt-amperes. One rating is for
purely resistive loads, and the other one takes the power
factor into account. A typical UPS rating might be 1440VA/865W.
Both ratings occur simultaneously, so 865W worth of light
bulbs can be used, or 1440VA at some power factor may be used.
You have to make sure your combination of loads, does not
exceed either rating.
The first couple of pages of this document, shows how you total
up both watts and VA, and compare to the rating of the equipment.
What they don't tell you, is a light bulb has the same watts as
VA, since a light bulb is purely resistive. A North American
ATX power supply, does not have power factor correction, so the
watts and VA have a ratio of 0.7 or 0.8. In Europe, active PFC
may be mandated for use with computers, so the ATX power supply
inside a European computer can have a power factor close to 1,
in which case there is no difference between the number used
for watts and for VA.
http://www.solidstatecontrolsinc.com/techhpapers/pdfs/upsplanninginstall.pdf
This page shows a picture of an ATX power supply with power
factor 0.7. This picture is not purely a power factor issue,
as the current waveform is also distorted (implying harmonics).
http://www.xbitlabs.com/articles/other/display/psu-methodology_8.html
The bottom picture of the ATX power supply on this page, shows
an active PFC corrected (European) power supply. The power
factor is very close to 1.0, and this kind of supply means that
the UPS VA rating will not be exceeded. A UPS powering one of
more of these, is more likely to "run out of watts".
http://www.xbitlabs.com/articles/other/display/psu-methodology_9.html
This document explains watts and VA a bit more:
http://www.apcmedia.com/salestools/SADE-5TNQYF_R0_EN.pdf
For the computer itself, you still have to figure out what power
it is consuming, and the APC selection tool does not take modern
gaming systems into account. A computer with two high end Crossfire
video cards (2x120W) plus an FX60 (120W) is not accounted for by
the tool. The APC tool mainly deals with business desktops, where
the video card is a $50 joke. APC concentrates on the processor
or processor(s) used. If you had a high end gaming system,
then working out the demands with a hand calculation would be
a better thing to do.
To work out the power, you would take the DC loading on the output
of the supply. Say it is 200W. The ATX supply has an efficiency
rating. Say it is 68% when the 200W load is connected. Now we
are at 294W. This would be 294W at the input, and if the supply
is not power factor corrected 294W/0.6 = 490VA. If there is
active PFC correction, 294W/0.98 = 300VA. And you have to decide
just what power factor (0.6, 0.7, 0.8) is appropriate for the
non-corrected case.
So the power factor for each piece of equipment is a big unknown.
And the label on the back of the equipment, generally lists such
a big current, as to be useless for estimating the size of UPS
needed. You either have to rely on the selection tool, or try
your hand at doing the calculation yourself.
In the case of the 1440VA/865W example above, the power factor
of all the loads would have to be less than 0.6, for you to
"run out of VA". But other UPS may have a different ratio between
their VA rating and their Watts.
That is my understanding at least. I don't do this for a living
Paul