For some reason, implied is that a 'whole house' protector
is the magic protection device. Protector is nothing more
than an electrical switch or an electrical wire. Protector is
trivial. Your attention has been diverted to the one thing
you can see. Protection - a different device - is important
and forgotten because it is not visible. Earth ground (into
the protectors) is the 'state of art' protection. You
suffered damage. Therefore something is wrong with your
'state of art' protection.
You suffered damage. Somehow a transient got inside the
house. It should not. Therefore your protection system has a
serious defect.
The 'whole house' protector is only secondary protection.
Start by inspecting your primary protection, if possible.
Pictures that demonstrate a defective primary protection
system:
http://www.tvtower.com/fpl.html
Now we move on to the secondary protection system. Does
every incoming utility make a 'less than ten foot' connection
to that SPG? If not (if any incoming utility wire connects to
some other earth ground), then you don't have effective
protection. For example, plug-in protectors (power strip and
UPS) make no 'less than 10 foot' connection from AC electric
to earth ground. Therefore they are ineffective AND may even
contribute to appliance surge damage. A protector is not
protection. Unfortunately you imply otherwise. A protector
is effective when it shunts (diverts, connects, acts like a
wire) the transient from each utility wire, less than 10 feet,
to the single point earth ground (SPG).
Your posted chart of cable connections implies you don't
understand how cable is surge protected. Cable needs no
connection to a 'whole house' protector. Cable should be
earthed to the same earth ground before even entering the
building. This even required by National Electrical Code
(NEC). A ground block that costs maybe $2 in Home Depot
connects that earthing wire to incoming cable. Cable company
should have installed it. The protector for cable is simply a
copper wire from ground block to earth ground rod. No 'whole
house' protector required for cable. What does a surge
protector becomes during a transient? An electrical wire.
Protection is defined by the earth ground rod - the SPG.
'State of the art' is not a protector. 'State of the art' is
defined by the quality of that SPG and how wires connect to
that SPG.
In the meantime, previously defined: those plug-in power
strip and UPS protectors are ineffective. They enrich the
manufacturer. Obviously. How far away is the SPG? More than
10 feet? So manufacturer forgets to mention they don't
protect from the destructive type of surge, such as you have
apparently suffered. That's correct. They only claim to
protect from a type of surge that does not typically exist and
that is made redundant by internal appliance protection. The
protector is only as effective as its earth ground. So
instead, the manufacturer remains dumb.
Is the computer protected? Then your diagram must show the
computer in relation to each single point earth ground. SPG
is the protection; not a power strip or APC UPS. Moreso,
those plug-in protectors can even contribute to damage of the
adjacent electronics. Your protection system has a problem.
So we suspect a problem with where protection is provided -
the SPG or connections to that SPG.
Earthing wire from protector to earth ground must be
separated from all other wires. For example, some think a
plug-in protector is earthed through the wall receptacle's
safety ground. How does that connection get made? A safety
ground wire is bundled with other wires. It can induce
transients onto those other wires. It is bundled with other
wires AND is too distant from SPG. Therefore the plug-in
protector is not earthed - does nothing effective.
Same might be true of your 'whole house' protector. How
does the wire route from protector to a single point earth
ground? Distance? Sharp bends? Through any conduit or other
metallic container? Bundled with what? No splices? Each
earthing wire must no be shared until all earthing wires
connect to the SPG. These are important questions answered by
a visual inspection. You suffered damage. Discover why the
system was compromised. How does each incoming utility wire
connect to that SPG?
What type of soil? A quality SPG (and not the protector) is
important. Many now install two earth ground rods - one being
insufficient - due to non-conductive soils. What makes a Ben
Franklin lightning rod effective? Not pointed rod verse blunt
rod. That was hype. Quality of the earth ground and how that
lighting rod connects to earth. Surge protectors are doing
same. A surge protector is only as effective as its earth
ground. So how good is your earthing soil?
If damage exists, then your earthing system may have
problems. Things often overlooked because the installer did
not understand, for example, the "less than 10 feet" concept.
Or because one incoming utility is using a separate earth
ground - very bad. Or because something geological has
compromised your single point earth ground. Your secondary
protection system (which defines the 'whole house' protector)
apparently has been compromised.
Nothing here should be 'over your head'. The complicated
stuff has been removed. An introduction to concepts was
posted previously at "Pull the wall plug or not?" in
nz.comp on 7 Sept 2004 at
http://tinyurl.com/5ttwl
Effective surge protection does same thing as the Ben
Franklin air terminal as taught in elementary school science.
Its not complicated other than following certain important
rules such as only one earth ground - the single point earth
ground. "Less than ten foot" from each incoming utility to
that SPG. But this we know even from your damage. The surge
did enter from outside. Your damage is typical of an
electrical circuit from cloud to earth. For some reason,
electricity had to find earth ground, destructively via your
cable network. Your damage is a classic example of surges
entering from outside.